Part Numbers D9068 (DACT Dialer), D9052 (Interface Module for Serial DACT Connect to the Morley Panel), D10024A, D10024, D9024, D8024 (Morley Fire Panels), D7033 and FMR-DACT-KEYPAD (Keypad Programmer for the D9068
*New Feature - Summary Fire Relay Option - GV2 Firmware 7.05 An option is added that changes the duration of the Panel Wide Summary Fire Relay output. Select GV2AUX→MISCELLANEOUS→Fire Summary Sustain: Yes: Summary Fire Relay clears when all Fire Alarms are cleared from the display. No: Summary Fire Relay clears when the area FireAlarms are silenced and all area Fire Points return to normal. The default option is No. This feature provides a way to maintain the fire strobes active after the alarm bell outputs are silenced.
Part numbersD7412GV2, D7412GV2, D9412GV2, D7212GV3, D7412GV3, D9412GV3, D7412GV4, D9412GV4, B8512G, B9512G
This feature blocks the programming feature through the keypad of the FPD-7024.
This feature is only enabled via RPS.
Step-by-step guide
1 Connect to the Panel via RPS an Open the FPD-7024 programming sheet.
2 Go into Program Accounts and Remote Access Security.
3 Open Anti-takeover Setting and Select "Lock all local programming (except Date/Time and all user PINs)" to block the programming via keypad of the panel.