Issue
Unable to activate smoke detectors into alarm with canned smoke. Even when everything is programmed and wired correctly.
Solution
Make sure the amount of D9067s polling loop cards are correctly setup in the panel. The Analog fire panel needs this information to be correct otherwise undesirable operation can result. In this case there were only four D9067s installed and the panel was set up to look for five. Once this was corrected, everything worked properly.