FLM-325-2i4, FPA-1000, FPA-1000UL, FPA-1000V2
How the FLM-325-2i4 Reports to the Central Station (CS).
The FLM-325-2i4 addressing using the D5070 Hand Held Programmer.
The FLM-325-2i4 is addressed as 1 address only.
The First input will display as xxx.1 on the panel keypad display, the Second input will display as xxx.2 on the panel keypad display.
It reports to the CS as xxx for the first input and xxx for the second input.
For the CS to destinguish between xxx.1 and xxx.2 it is recommended to program each input as a different function.
Example: Point 017
Program 017.1 as a Fire Input and program 017.2 as a Supervisory.
Now the CS will receive a Point 017 as either a Fire Alarm or Trouble for the First input and a Supervisory Alarm or Trouble for the second input. Just keep in mind the CS can only get the 017 it does not have the ability to report the .1 or the .2.