Issue
When using two D192C or D192G modules for audible silence the system will not trigger relay B when a fire alarm is activated.
Solution
The point index for point 3 and relay B in Relay Parameters has not been programmed correctly.
Ensure the D136 is plugged in the ALT. Bell Socket 3 pins up, 2 pins down.
You will need to edit the point index that is assigned to point 3 for relay “A” and relay parameters for relay “B”.
- With your D5200, copy 9000 MAIN from the panel.
- Go to Relay Parameters – Panel Wide Relays, and place a “B” into summary alarm.
- Then go to Area Wide Relays, and make sure that there is an “A” for Fire Bell.
- There should be a zero for Alarm Bell.
- Send changes to panel.
- Copy RADXPNTS from the panel.
- Program points 1 and 2 with a zero for the type, a nine for the response, a two for buzz on fault, and fire point as Yes.
- All of the other options will be a No.
- For point three, which is wired to relay “A” edit the index as follows.
- The type will be a zero, the response will be a 2, and local while armed and disarmed will be a Yes.
- All of the other options for that index will be a No.
- Program the text for point three to say PRESS COMMAND 4.
- Relay “B” provides the trigger voltage for the strobes from the D192C or "G".
- Relay “A” provides the trigger voltage for the horns from the other D192C or "G".
- When a point is in fire alarm both D192C’s or "G's" will have 13.7vdc to the output.
- Once alarm silence is pressed or a valid code is entered then relay “A” will silence, and relay “B” will stay energized.
- In order to silence relay “B” press command 4 or passcode + escape.
Part numbers D192C, D192G, D7212, D7412,D9112, D9124, D9412, D7212G, D7412G, D9112G, D9124G, D9412G