FPD-7024 - A Maximum of 4 FPP-RNAC-8A-4C can be added to the Option Bus.
FPP-RNAC-8A-4C Dipswitch Settings
All Dipswitches OFF on Dipswitch Bank S1
Dipswitch Bank S2 - Dipswitch 0 Off - Dipswitches 1 & 2 set the AC Failure Delay
Dipswitches | 0 | 1 | 2 |
No Delay | Off | Off | Off |
1 Hour Delay | Off | Off | On |
3 Hour Delay | Off | On | Off |
6 Hour Delay | Off | On | On |
Dipswitched 3,4,5,and 6 Set the option Bus Address
Dipswitches | 3 | 4 | 5 | 6 |
Disabled | Off | Off | Off | Off |
Address 1 | Off | Off | Off | On |
Address 2 | Off | Off | On | Off |
Address 3 | Off | Off | On | On |
Address 4 | Off | On | Off | Off |
Address 5 | Off | On | Off | On |
Address 6 | Off | On | On | Off |
Address 7 | Off | On | On | On |
Address 8 | On | Off | Off | Off |
Address 9 | On | Off | Off | On |
Address 10 | On | Off | On | Off |
Address 11 | On | Off | On | On |
Address 12 | On | On | Off | Off |
Address 13 | On | On | Off | On |
Address 14 | On | On | On | Off |
Address 15 | - | - | - | - |
*Note - Each device on the option bus of the FPD-7024 requires a unique address.
FPD-7024 Panel ProgrammingEnter Program Mode on the FPD-7024
1.) Press 0 and Enter your program pin (Default is 9876). The display should read Program Modes on the top line of the display. 2.) Press 3 for Program System
3.) Press 4 for Option Bus
4.) Press 1 for Update Bus *** The keypad will display “Updating . . . TOT BUS DEVS: XX”. "XX" = the total number of devices on the Option bus. If (00) or the incorrect total number of devices on the bus appears, check the wiring and addressing of each device on the Option bus. Each Device needs to have a unique address. Then repeat steps above until all the devices are learned to the Option Bus of the panel. ***
5.) To Exit Programming, press the "*/Back" button 4 times
**NOTE: Panel NAC outputs will not be in sync with the NAC output devices connected the the FPP-RNAC-8A-4C.
FPA-1000 - A Maximum of 4 FPP-RNAC-8A-4C can be added to the Option Bus
All Dipswitches OFF on Dipswitch Bank S1
Dipswitch Bank S2 Dipswitch 0 Off -Dipswitches 1 & 2 set the AC Failure Delay
Dipswitches | 0 | 1 | 2 |
No Delay | Off | Off | Off |
1 Hour Delay | Off | Off | On |
3 Hour Delay | Off | On | Off |
6 Hour Delay | Off | On | On |
Dipswitched 3,4,5,and 6 Set the option Bus Address
Address 11 | On | Off | On | On |
Address 12 | On | On | Off | Off |
Address 13 | On | On | Off | On |
Address 14 | On | On | On | Off |
**NOTE: Panel NAC outputs will not be in sync with the NAC output devices connected the the FPP-RNAC-8A-4C.