Overview
Local mean it does not send reports to Central Station - It is only anunciated locally.
Local While Disarmed
Default:
- Point Indexes 1 to 8: No
- Point Index 9: Yes
- Point Indexes 10 to 11: No
- Point Index 12: Yes
- Point Indexes 13 to 31: No
Selections: Yes/No
Parameter Description
Use this parameter to allow a controlled point (P## Type 1, 2, 3 ), to report alarms, troubles and restoral reports only when the area is armed. This parameter does not affect local annunciation.
IMPORTANT:
- This parameter suppresses all reports from 24-hour points. Do not use this parameter with Point Type 0. This parameter only works for disarmed points, and a Type 0 is a 24 hour "always armed" point. Instead, choose any type other than 0, and use a point response that sends an alarm whether the point is armed or not. For instance, Point Type 1 and Point Response 9 send an alarm on a trouble or a short (I) whether the area is armed or not.
- This parameter affects keyswitch points and suppresses keyswitch (troubles/restorals) and D279 (alarms/troubles/restorals) Do not use this parameter for these applications.
- To meet UL864 requirements for central station and remote station applications, set this parameter to No.
Parameter Options
- Yes:Suppress alarm, trouble and restoral reports from this point while the area it is assigned to is disarmed.
- No:Report events occurring from this point while the area is disarmed.
Local While Armed
Default: No
Selections: Yes/No
Parameter Description
Use this parameter to allow a controlled point (Point Types 1, 2, or 3), to report alarms, troubles and restoral reports only when the area is disarmed. This parameter does not affect local annunciation.
IMPORTANT:
- This parameter suppresses all reports from 24-hour points. Do not use this parameter with Point Type 0. This parameter only works for disarmed points, and a Type 0 is a 24 hour "always armed" point. Instead, choose any type other than 0, and use a point response that sends an alarm whether the point is armed or not. For instance, Point Type 1 and Point Response 9 send an alarm on a trouble or a short (I) whether the area is disarmed or not.
- This parameter affects keyswitch points and suppresses keyswitch (alarms/troubles/restorals) and D279 (opening/closing/troubles/restorals) Do not use this parameter for controlled points that arm/disarm.
- To meet UL864 requirements for central station and remote station applications, set this parameter to No.
Parameter Options
- Yes:Suppress alarm, trouble and restoral reports from this point while the area it is assigned to is armed.
No: Report events occurring from this point while the area is armed.
Part numbers D7212B, D9112B, D7212B1, D9112B1, D7212, D7412, D9112, D9124, D9412, D7412G, D7412G, D9124G, D9412G, D7412GV2, D7412GV2, D9124GV2, D9412GV2, D7412GV3,D7412GV3, D9412GV3, D7412GV4, D7412GV4, D9412GV4, B8512G, B9512G