Issue - What effect does alarm verification have on the point?
Solution - When an Alarm Verification point enters into alarm, the control panel removes power from all Resettable points for the duration programmed in A# Verify Time. When power is reapplied, a 60-second confirmation window begins. If the detector is still in alarm and experiences another alarm during the confirmation window, or a different Resettable Verification point in the area sense a alarm, an alarm occurs.
Unverified Event report is not related to A# Verify Time. Unverified events are for cross points. Do not enable Cross Point if Alarm Verify is enabled.
Part numbers D7212,D7412, D9112, D9124, D9412, D7212G,D7412G, D9112G, D9124G, D9412G, D7212GV2,D7412GV2, D9124GV2, D9412GV2, D7412GV3, D9412GV3, D7412GV4, D9412GV4, B8512G, B9512G