Issue
When relay response type is set to 1 in a point index configured for fire, the point relay is toggling when a CMD 47 is done.
Solution
This is because a relay response type of 1 will folow any off normal condition of a point.
Selections: Blank, 1 - 2
1) Relay Follow Point: The relay corresponding with this point will activate when the point is faulted to any off normal condition. The relay will automatically reset when the point is returned to normal.
2) Relay Latches: The relay corresponding with this point will latch when the point goes into an alarm condition. This relay provides a steady output until the alarm is acknowledged by a valid passcode then cleared from alarm memory with an acknowledgment at the command center.
Application Note: Point 128 is reserved for use other than an actual point. Only the first 127 points can have an associated relay. Relays are not available for points 129 to 247.