    How to Program FPD-7024 to Report Via Network

    FPD-7024 Keypad programming to Setup Network Card

    * Note: The panel mother should be RED with a Firmware reversion of 1.03 to support Ethernet communications.

     Connect the Network card to the option bus. (*The DX4020 needs to be addressed as 250, all switches On / CLOSED.) connected to the panel. B420 and B426 Set the Rotary Switch to 9 = Address 250

    Keypad Programming Steps

    1) Press 0 Enter 9876

    2) Press 3 Program System

    3) Press 4 Option Bus

    4) Press 1 Update Bus – The keypad will display “Updating . . .  TOT BUS DEVS: XX”. XX = the total number of devices on the Optionbus.      If 00 or not the correct total number of devices on the bus, check the wiring and addressing of each device on the Option bus. Each Device needs to have it own address. Repeat steps 3 and 4 until all the devices learned in the panel.

    5) Press 7 Remote Program

    6) Press 1 Enable

    7) Press the * / Back key Once the top line of the display should read “PROG MODES”.

    😎 Press 6 Program Accounts

    9) Press 7 Alternate Communication – Select 0 Network

    10) Press * / Back key once

    11) Press 5 Communication Attempts Enter 05 #

    12) Press 1 Phone / IP Number

    13) Press 1 Phone / IP 1

    14) Press 1 Enter 0 to tell the panel this is an IP Address (then enter the 12th digit IP Address of the Central Station) followed by the ACK Wait 015 -  then the Poll Rate 180 followed by Anti - Replay 1#Enter. The complete string would be01730840330820151801 if reporting to IP 173.84.33.82 with 5 Minute Supervision.

    15) Press 2 Port Number Enter 07700#Enter (Default Port) or Port number used by the Central Station

    16) Press 3 Format Select 7 Modem Format

    17) Press 4 Account Number (enter you 4 digit account number followed by #)

    18) Press the * / Back key Once the top line of the display should read “Phone / IP Number”


    Setting a Second IP address (if necessary)

    If reporting via IP the second path needs to be a different receiver, not the same receiver with 2 IP addresses to it.

    1) Press 2 Phone / IP 2 to setup a second IP address if needed

    2) Press 1 Enter 0 to tell the panel this is an IP Address (then enter the 12th digit IP Address of the Central Station) followed by 0151801#Enter

    3) Press 2 Port Number Enter 07700#Enter (Default Port) or Port number used by the Central Station

    4) Press 3 Format Select 7 Modem Format

    5) Press 4 Account Number (enter you 4 digit account number followed by #)

    6) Press the * / Back key Twice the top line of the display should read “Program Accounts

    7) Press 4 Ring Count Enter 02 #

    😎 Press 7 Alternate Communications

    9) Press 0 Network

    10) Press the * / Back key 4 times to return to System Normal.

    **NOTE: If only using one IP path to the CS, Program Report Steering to PHONE 1 ONLY

    1)   Press 0 Enter 9876

    2)   Press 6 Program Accounts

    3)   Press 3 Report Steering

    4)   Press 11

    5)   Press 21

    6)   Press 31

    7)   Press 41 

    😎   Press 51     

    9)  Press 61 

    10)  Press 71 

    11)  Press 81

    12)  Press 91 

    13) Press the * / Back key 4 times to System Normal


    DX4020 Telnet Settings

    Note: The EPROM version of the DX4020 must be 2.21 or higher to be compatible with the FPD-7024.

    Now that the FPD-7024 is configured properly, the DX4020 needs to be programmed (telneted) to communicate with it. Refer to the DX4020 Installation Guide for more detailed instructions on DX4020 programming.

    The DX4020 needs to be address 250 all dip-switches closed.

    Channel 1 Parameters
    Baud rate - 9600

    IF Mode - 4C

    Flow - 00

    Port – 7700 (Default Port)

    Connect Mode - CC

    Data gram – 02

    Version history
    Last update:
    ‎04-06-2023 07:15 PM
    Updated by:
    Contributors
    Icon--AD-black-48x48Icon--address-consumer-data-black-48x48Icon--appointment-black-48x48Icon--back-left-black-48x48Icon--calendar-black-48x48Icon--center-alignedIcon--Checkbox-checkIcon--clock-black-48x48Icon--close-black-48x48Icon--compare-black-48x48Icon--confirmation-black-48x48Icon--dealer-details-black-48x48Icon--delete-black-48x48Icon--delivery-black-48x48Icon--down-black-48x48Icon--download-black-48x48Ic-OverlayAlertIcon--externallink-black-48x48Icon-Filledforward-right_adjustedIcon--grid-view-black-48x48IC_gd_Check-Circle170821_Icons_Community170823_Bosch_Icons170823_Bosch_Icons170821_Icons_CommunityIC-logout170821_Icons_Community170825_Bosch_Icons170821_Icons_CommunityIC-shopping-cart2170821_Icons_CommunityIC-upIC_UserIcon--imageIcon--info-i-black-48x48Icon--left-alignedIcon--Less-minimize-black-48x48Icon-FilledIcon--List-Check-grennIcon--List-Check-blackIcon--List-Cross-blackIcon--list-view-mobile-black-48x48Icon--list-view-black-48x48Icon--More-Maximize-black-48x48Icon--my-product-black-48x48Icon--newsletter-black-48x48Icon--payment-black-48x48Icon--print-black-48x48Icon--promotion-black-48x48Icon--registration-black-48x48Icon--Reset-black-48x48Icon--right-alignedshare-circle1Icon--share-black-48x48Icon--shopping-bag-black-48x48Icon-shopping-cartIcon--start-play-black-48x48Icon--store-locator-black-48x48Ic-OverlayAlertIcon--summary-black-48x48tumblrIcon-FilledvineIc-OverlayAlertwhishlist