Issue
The panel is not sending alarms for a 24 hour intrusion point that is set up for local while disarmed. When the panel is armed the alarm for the zone is received on the keypad but it does not dial out.
Solution
Set the index as a type 1 and a response of 9, instead of a type 0 with a response of 0, and it should work correctly. Local While Disarmed suppresses all reports from 24-hour points. Do not use P## Type 0 for this prompt.
Remember, this only works for disarmed points, and a Type 0 is a 24 hour "always armed" point. Instead, choose any Type other than 0, and use a point response that will report an alarm whether the point is armed or not.
For instance, P## type 1 and response 9 will report an alarm on an open or a short (I) whether the area is armed or not.