Issue
How do I program the test report on a 9000, G, or GV2 series panel?
Solution
- Using a D5200 programmer, copy the program using the RADXSKED (version 1.04) handler.
- Enter group on SKEDS.
- Go to the Sked number that you would like to use for the test report by entering the Sked Number then pressing the white ENTER button.
- For the function code, enter 9
- After pressing Enter, you will be presented with two options - Defer Test and Hourly Report. In most cases these should be left to no and you can press Exit Group to get back. For more information about these options, see the Program Entry Guide for the panel with which you are working.
- For the Time entry, enter the time that you would like the test report to send. The time should be entered in military time.
- The Date entry should be left blank.
- Set every day of the week to Yes.
- Set Xept Holiday to No
The Holiday entries do not apply if Xept Holiday is set to No, so don't worry about how they are set.
Part numbers D7212, D7412, D9112, D9124, D9412, D7412G, D9124G, D9412G, D7412GV2, D9124GV2, D9412GV2, D7412GV3, D9412GV3