Issue
When the program is copied from the DACT, why is the Time to Report always set 00:00?
Solution
Each time the programmer is connected and the program is copied from the DACT it will set the count down timer for the test report to 12 hours and the display of the programmer will have Hour to Report set at 00:00. The test report will send 12 hours from the program change. Then every 24 hours after that.
Part numbers D2071A, DS9471, 911A, 911AC, D2071AC, D2071AHC, D2071ACPL-1, D2071ACT, D2071AH, HDCP-3, D5050, D5200