Issue
The relays are not resetting after the alarm, we have to retrip the alarm a second time to get the relay to reset.
Solution
It has been observed that relay modules assigned to high address numbers, do not always turn off when the Fire Alarm Control Panel (FACP) is reset.
In order to ensure that all relays turn off reliably, it is recommended that these devices be installed at addresses below 56.