Issue
Addressable point will not activate into alarm.
Solution
Panel may have been configured for more loops than are actually being used.
1: Enter Commission mode.
2: Press Yes twice for more options.
3: Press 2 for Setup Options.
4: Press Yes twice to get to “Quantity of Loop Drivers”.
5: Set the correct number. Press Yes.
6: Set device type to Hochiki ESP.
7: Press Yes to scroll through the rest of the setup options.
8: Press No once out of the setup options menu.
9: Press 1 for configure.
10: Press 1 for loop one, then 3 for auto learn.
11: Press YES once.
12: Repeat steps 10 and 11 until all of the loops have been auto-learned.
13: When all loops have been auto learned in proceed to exit panel programming by selecting Normal Operation from the main menu.
14: Test all detectors.
Part numbers D8024, D9024, D10024, D10024A, D323A, D324A, D325A, D326A, D339A