Issue
When AC power is lost on all 6 - D7038's it causes NAC1 on the D7024 that is driving the inputs of the D7038's to go into trouble. What is causing this to happen?
Solution
The AC dipswitches 2 & 3 on the D7038's all had different settings. In order for the AC Delay feature to work, all the AC dipswitches 2 & 3 need to be set for the same value.
Note: In order for Dip Switch Changes to take effect the D7038 needs to be powered down completely for 4 minutes.
Dip Switch Setting For AC Fail Delay
Delay Time (In Hours) Dip Switch (2) Dip Switch (3)
AC Fail Time Delay (1) On/Closed Off/Open
AC Fail Time Delay (6) Off/Open Off/Open
AC Fail Time Delay (12) Off/Open On/Closed
AC Fail Time Delay (24) On/Closed On/Closed
Part numbers DS9400, DS9400I, DS9400M, D7024, DS9484, D7038