On the DS9400, DS9400M, D7024, and FPD-7024 Fire Alarm Panels the Water-Flow timer can be set from 0.5 seconds (fast) up to 89 seconds. This timer feature is programed in Program Points > Point Functions. Only One Point Function timer can be set. (Example - if function 4 as a Loop Response Timer set to 16 seconds and you add a second function like function 12 with a Loop Response Timer of 60 Seconds - Both Function 4 and Function 12 will have a Loop Response Timer of 60 Seconds. Now if a third function is added like function 2 with a Loop Response Timer of 30 Seconds, now Functions 2, 4, and 12 will have a Loop Response Timer of 30 Seconds.
*Note: A limit of 20 points may be assigned to point functions that have been programmed with a response time other than 0.5 seconds (Fast).