Install a 1K Ohm Resistor in parallel with the zone outputs and common on the C8137. Program the on the C601 as input type 2. Program the zn#polar is a 0. Put the P-1 jumper (3 pin jumper) on the two pins farthest from the Telco connections. The zone will respond to Alarm on Short and Trouble on Open.