Issue
Area armed relay energizes when the exit time expires.
Solution
Beginning with revision 5.27, Programming a 64 in Area 8’s Silent Alarm Relay will cause Area Armed Relay to energize at the beginning of the exit delay. Prior to revision 5.27, area armed relay only energizes at the end of the exit time.
The relay activates when the specified area becomes master armed. The relay remains activated until the area is disarmed, it will not deactivate during the entry delay time.
If multiple areas use the same relay, the relay activates when all areas are armed. It deactivates when the first area disarms.
Part numbers D7212, D7412, D9112, D9124, D9412, D7412G, D7412G, D9124G, D9412G, D7412GV2, D7412GV2, D9124GV2, D9412GV2, D7412GV3,D7412GV3, D9412GV3,