Issue
This is normal if the panel is programmed not to send restorals.
In RAM/RPS check in the following:
Point Index Codes > Point Indexes 1-16 or Point Indexes 17-31
Default: No Selections: Yes or No
Yes: Disable restoral reports for this point.
No: Enable restoral reports for this point. When this option is enabled, a restoral report is sent to the receiver when the point returns to normal after being in an alarm or trouble condition.
If you are using the 5200:
In the 5200 check under:
Default: No
Selection: Yes or No
Yes = Disable Restoralreports for this point.
No = Enable Restoralreports for this point.
When this option is enabled, a Restoral report is sent to the receiver when the point returns to normal after being in an alarm or trouble condition. Use this item to automatically put this point back into the system.