Issue
The FA113 will not arm the panel if it was disarmed from the keypad and will not disarm if panel was armed from the keypad
Solution
Used as an arm/disarm device, the FA113 is configured to panel zone 74 or 194. Pressing the FA113 Off button sends an OPEN signal to the control panel and pressing the On button sends a NORMAL signal to the control panel.
The area should be both Armed and Disarmed by the FA113 for it to function correctly. When the arming state is changed by the FA113, then by another means, the FA113 becomes unable to detect the current armed state of the area and will not respond to the keys pressed.
Correct settings for FA113:
The transition of the state of point 74 is what causes the area to arm or disarm.
• Mode in the D8125INV is set to 4.
• Keyswitch Maintained point (Point Type 4) with Point Response 2, is required for the FA113.
• Area will arm with a transition from open to normal on point 74.
• Area will disarm with a transition from normal to open on point 74.
The FA113 is also used for panic on point 75 (7412G) and point 195 (9412G).