Configure the IP Communicator for the panel:
- Set the address switch for 1 or 2 making sure to not duplicate an already used IP communicator address.
- Connect to the SDI2 bus using either a 4-pin molex connector or 4-conductor cable to terminals 33-36 (do not connect using both the 4-pin molex and 4-conductor).
When using B920 or B930 SDI2 type Keypads:
- Enter the installer code (default-123) and press Enter.
- Press 1 (Installer Menu).
- Press 1 (Programming Menu).
- Press 2 (Network Menu).
- Press 1 for Bus module (1) Menu (or 2 for Bus module (2) Menu).
- Press 1 for Module Parameters
- Press 1 to edit DHCP, the keypad displays Set DHCP Enable with the current setting Yes/No.
- Press NEXT until the keypad displays: Set DHCP Enabled=No, and press ENTER. The keypad displays Parameter Saved and returns to [Press 1 to edit DHCP Enable] with the changed setting.
- Press ESC to view Module Param Menu
- Press 2 for Address Param Menu, press 1 to edit the IP address.
- The display reads: [edit IP address?] with the current setting. Press Enter to edit the IP address.
- Enter the first Octet and press Next…….
- Enter the second Octet.
- Enter the third Octet.
- Enter the fourth Octet and press Enter. The keypad says Parameter Saved and returns to the [Edit IP Address?] Display. Press ESC.
- Press 2 to edit the Subnet Mask. The display reads [edit subnet mask?], with the current setting.
- Perform steps 11a-d.
- Press 3 to edit the Default Gateway. The display reads [edit default gateway?], with the current setting.
- Press ENTER to edit the Default Gateway.
- Perform steps 11a-d.
- Press Escape to exit keypad programming.
When using D1255 or D1260 SDI type keypads:
- Press 99 ENT
- Press NEXT to access the TOOLS MENU? display. Select [ENT], (D1260: use soft-key)
- Enter the Installer Passcode and press ENT (default=123)
- The display reads PROGRAMMING: Select [ENT], (D1260: use soft-key)
- Press NEXT to access the IP MODULE CONFIG display: Select [ENT], (D1260: use soft-key)
- At the B420 MOD 1-2? prompt, enter press 1 ENT
- MODULE PARAM displays, select [ENT], (D1260: use soft-key)
- Continue with steps for D1255 or D1260 below:
Using the D1255:
- The display reads DHCP ENABLE; press [ENT].
- The display reads MODULE [#] DHCP (YES / NO) alternating with the current setting.
- Press ENT followed by NEXT until NO displays and press ENT.
- The display reads PARAMETER SAVED alternating with the changed setting, Press ESC 2x to reach MODULE PARAMS.
- Press NEXT to reach ADDRESS PARAMS, press ENT to select and ENT again to select IP Address.
- The display reads MOD [#] ADDRESS alternating with the current IP Address.
- Press ENT again to change the setting. The display is ready to change the first Octet.
- Enter the 1st Octet (xxx) and press NEXT.
- Enter the 2nd Octet (xxx) and press NEXT.
- Enter the 3rd Octet (xxx) and press NEXT.
- Enter the 4th Octet (xxx) and press ENT, the display reads PARAMETER SAVED alternating with MOD [#] and the changed setting.
- Note: Digits can be deleted by pressing the PREV
- Press ESC the display reads IP ADDRESS, press NEXT to display SUBNET MASK.
- Press ENT to Select Subnet Mask, the display reads Mod [#] SUBNET alternating with the current Subnet Mask. Press enter to change the Subnet Mask.
- Perform steps [7a. – d.] to change the Subnet Mask.
- Press ESC, the display reads IP ADDRESS. Press NEXT (2x) to reach DEFAULT GATEWAY.
- Press ENT to select Default Gateway, the display reads; Mod [#] GATEWAY alternating with the current Default Gateway setting. Press ENT to change the Default Gateway.
- Perform steps [7a. – d.] to enter the Default Gateway.
- Press ESC until programming is exited.
Using the D1260:
- The display reads DHCP Enable / UP&P Enable; Select DHCP ENABLE
- The display reads Module [#] DHCP Enabled with current setting (Yes or No), press Edit, select No and select Save.
- Display reads [Parameter Saved] and returns to Module [#] DHCP Enabled with the changed setting.
- Press Exit 2x and select ADDRESS PARAMETERS.
- Select IP Address. The display reads: Module [#] Address with current address [default= 0.0.0.0].
- Press Edit to change the setting. The display is ready to change the first Octet.
- Enter the 1st Octet (xxx) and press Next
- Enter the 2nd Octet (xxx) and press Next
- Enter the 3rd Octet (xxx) and press Next
- Enter the 4th Octet (xxx) and press Save, the display reads Parameter Saved and returns to Module [#] Address with the changed setting.
- Press Exit and select SUBNET MASK.
- Press Edit to change the Subnet Mask.
- Perform steps [6a. – d.] to enter the Subnet Mask
- Press Exit and select DEFAULT GATEWAY.
- Press Edit to change the Default Gateway.
- Perform steps [6a. – d.] to enter the Default Gateway.
- Press Escape until programming is exited.