Connect the 4-wire smoke detector Alarm Loop terminals to any supervised point. Route power through a D133 (or D134) Relay Module using the following connections:
Relay X1+ to Panel Aux+
Relay X1- to Panel Ext1
Relay N/C1 to Panel Aux+
Relay COMM1 to Smoke Power +
Smoke Power - to panel Aux -
Note: When using D134 relays, the connection points X2+ X2-, N/C2, COMM2, etc. can be substituted for or X1+ X1-, N/C1, COMM1, etc.
The control panel’s external relay output EXT1 must be programmed for the reset function (EXT1 or EXT2).
Set Relay Logic to Function One Only
Set Function One to RESET
Resetting the System
Resetting the system takes about 20 seconds. If points do not reset, contact your alarm company for help. To reset:
Ensure the system is off (On light is off).
Press the [3] key. The display shows the following:
ENTER CODE TO RESET SENSORS
Enter your passcode (Owner type passcode required). Resetting begins and the display shows the below; this procedure takes about 20 seconds:
RESETTING...
After the system resets, the display returns to the off state.