This point type monitors the AC power of an auxiliary power supply. When the point is in an off-normal state, the control panel waits for the time programmed in AC Fail Time before generating a Point Trouble. If Fire Point is set to Yes, the off-normal condition results in a Fire Trouble. This point type does not use Point Response; therefore, no alarm condition occurs.
The point will generate a point trouble instantanously, but the reporting of the point will be delayed for the amount of time programmed in AC fail time located in Panel Wide Parameters > Power Supervision.