AC Fail/Res Rpt
Default: No
Selections: Yes/No
Parameter Description: AC Power Supervision reports are sent to the central station and local printer at the time programmed for AC Fail Time.
IMPORTANT: To comply with NFPA standards and UL 864 requirements for Commercial Fire Systems, program this item NO and program AC Tag Along as YES.
Parameter Options
Programming Instructions
D5200 Programming
1) Receive copy of 9000MAIN
2) Enter group PANEL WIDE PARAMETER
3) Enter group Power Supervision
4) Fail/Res Rpt Yes/No (SPACE bar to change)
*Must press ENTER for each prompt entry
5) Send Load to panel