Discharge Cycle |
|
AC Off |
AC Fail Report when AC fails, if the control panel is programmed to report AC failure at occurrence. |
13.9 VDC |
Charging float level. |
13.8 VDC |
Charging status LED on. |
12.0 VDC |
Low Battery and AC Fail Reports if programmed. Low battery LED on. |
10.0 VDC |
Battery load shed (processing functions continue if AC is present). |
Recharge Cycle |
|
AC On |
Load shed relay reset; battery charging begins; Battery Trouble and AC Restoral Reports are sent. |
13.7 VDC |
Battery Restoral Reports are sent. Low battery LED off. |
13.9 VDC |
Changing status LED off; battery float charged. |
Charging Status and Low Battery LEDs |
|||
Type |
LED |
Action |
|
Color |
State |
||
Charging Status LED |
Yellow |
|
Shows the charging status of the battery. |
|
Yellow |
Off |
Battery is fully charged. If the battery is missing, shorted, or reversed, the Charging Status LED is off, but the red Low Battery LED is flashing. |
|
Yellow |
On |
Battery float charge is below 13.8 VDC. If AC is present, the battery is charging. Indicates the combined current draw from all outputs exceeds 1.4 A. This is normal under alarm conditions for non-fire systems with sirens or bells drawing more than 1.4 A. If the LED lights regularly for extended periods or does not go out, check the current draw for devices connected to the power outputs. |
|
Yellow |
Flash once per minute |
System is checking the battery. |
Low Battery LED |
Red |
|
Shows the condition of the battery. |
|
Red |
Off |
Battery is fully charged. |
|
Red |
On |
Battery voltage dropped to between 12.0 VDC and 11.8 VDC. LED turns off when voltage reaches 13.7 VDC. |
|
Red |
Flash |
Battery is missing or shorted. |