Answer
· In Config Browser create a connection Access Engine and add an AMC 4-W
· Add a new entrance to this AMC
- select an entrance model (e.g. DM 01b)
- select 1st inbound reader "WIE1K Reader: Wiegand Reader, keyboard"
- click ok
· Activate pincode verification
- click on the reader ("WIE1K Reader")
- select tab Settings
- set "PIN code required" option to "PIN code turned on"
· Activate new configuration
- apply changes
- Start BIS (or reload config) in BIS manager
· Create an access Authorization that includes this reader
- log in into BIS user interface
- open Access Engine
- go to System data-> Access authorizations and create new authorization
- assign the before created door model to this authorization
· Configure cardholder
- go to Personnel data-> Persons and create a new person
- go to Personnel data-> Cards and record a card
- go to Personnel data-> Cards and assign the before created access Authorization
- go to Personnel data-> PIN code and enter a PIN (6 digits)
· Test configuration
- present card-> LED is flickering green/red
file:///C/...rs/lsr9fp/AppData/Local/Temp/How%20to%20configure%20the%20keypad%20reader%20RK-40%20with%20pin%20code.html[5/21/2018 11:30:16 AM]
- enter 6 digit PIN-> LED switches to permanent green and door is opened if PIN is correct
Notes:
- The pincode is recognized as "Alarm PIN" if it is increased by 1 (112234 instead of 112233) or
· if it is mirrored (332211 instead of 112233)
- If the reader does not react on an entered PIN even if the LED is flickering it may have the
wrong configuration
· Reason: The same reader hardware is sold with two different configurations:
- 4.998.127.615 ARD-RK40 to be connected with APC-DC202 (=BoGuard32 controller; do
not order this)
- F.01U.514.655 ARD-RK40-AMC01 to be connected with AMC-4W ("our" AMC)
· The problem can be fixed with a configuration card.
· Steps to perform:
- disconnect reader from AMC
- hold configuration card in front of the reader
- connect reader to AMC --> you will hear a special acoustic signal ("double beep")
- move configuration card out of the reader's range --> reader will reboot and has now the correct
configuration permanently stored.
- disconnect reader from AMC