    Bosch control panels communicate with a network receiver using either Onboard IP, a cellular card attached to the panel, a B426, B450 or DX4020 (SDI only) network communicator, depending on the panel type. When troubleshooting, the physical address of the network communicator and which path (1-4) was used for communication, are used to isolate the problem. Different methods are used to display the physical address and path depending on the type of panel experiencing the problem. This article explains how to interpret the keypad display on different panel types.

    • Network interface when used on the SDI bus:
      • Legacy SDI panels addressed the B426 or DX4020 as SDI 88 or SDI 92 (GV3). The SDI xx report indicates both the network communicator address and the path number.
      • When addressed as SDI 88 the path number is indicated by incrementing SDI 88 as 88-91.
        • Network communicator addressed as SDI 88:
          • SDI 88 = path 1
          • SDI 89 = path 2
          • SDI 90 = path 3
          • SDI 91 = path 4
        • When addressed as SDI 92 the path number is indicated by incrementing SDI 92 as 92-95.
          • Network communicator addressed as SDI 92:
            • SDI 92 = path 1
            • SDI 93 = path 2
            • SDI 94 = path 3
            • SDI 95 = path 4

    Device             Message                                              Failing to Poll on:  
    SDI 88             Comm Trouble / Fail SDI 88              Address 88, Path 1
    SDI 88             Comm Trouble / Fail SDI 89              Address 88, Path 2
    SDI 88             Comm Trouble / Fail SDI 90              Address 88, Path 3
    SDI 88             Comm Trouble / Fail SDI 91              Address 88, Path 4

    SDI 92             Comm Trouble / Fail SDI 92              Address 92, Path 1
    SDI 92             Comm Trouble / Fail SDI 93              Address 92, Path 2
    SDI 92             Comm Trouble / Fail SDI 94              Address 92, Path 3
    SDI 92             Comm Trouble / Fail SDI 95              Address 92, Path 4

    • Network interface when used on the SDI2 bus:
      • The B426 or B450 is addressed as 1 or 2 when connected to the SDI 2 bus (refer to the device IOG for address configuration). The first digit indicates the path number, and the second digit indicates the B426 or B450 address.

    Device-Addr                          Message                                  Failing to Poll on:
    SDI 2-Addr1               Comm Trouble / Fail SDI 11              Path 1, Address 1
    SDI 2-Addr1               Comm Trouble / Fail SDI 21              Path 2, Address 1
    SDI 2-Addr1               Comm Trouble / Fail SDI 31              Path 3, Address 1
    SDI 2-Addr1               Comm Trouble / Fail SDI 41              Path 4, Address 1

    SDI 2-Addr2               Comm Trouble / Fail SDI 12              Path 1, Address 2
    SDI 2-Addr2               Comm Trouble / Fail SDI 22              Path 2, Address 2
    SDI 2-Addr2               Comm Trouble / Fail SDI 32              Path 3, Address 2
    SDI 2-Addr2               Comm Trouble / Fail SDI 42              Path 4, Address 2

    • New G Series (B8512G/B9512G) and B Series panels using Onboard Ethernet or Cellular:
      • Panel onboard IP displays address 0, plug-in Cellular displays address 8. The first digit indicates the path # and the second digit indicates the communicator address.
      • When using the B426 or B450 on the SDI 2 bus the display will be the same as previously described.

    Device                         Message                                  Failing to Poll on:    
    Onboard Ethernet       Comm Trouble SDI 10           Path 1, Address 0
    Onboard Ethernet       Comm Trouble SDI 20           Path 2, Address 0
    Onboard Ethernet       Comm Trouble SDI 30           Path 3, Address 0
    Onboard Ethernet       Comm Trouble SDI 40           Path 4, Address 0

    Onboard Cellular         Comm Trouble SDI 18           Path 1, Address 8
    Onboard Cellular         Comm Trouble SDI 28           Path 2, Address 8
    Onboard Cellular         Comm Trouble SDI 38           Path 3, Address 8
    Onboard Cellular         Comm Trouble SDI 48           Path 4, Address 8

    • Comm Trouble: Displays when the panel is not receiving an acknowledgement from the receiver prior to making retry attempts.
    • Comm Fail:   Displays when the panel has not received an acknowledgement from the receiver prior to exhausting all of the programmed retry attempts.
    • How to calculate the network supervision interval

    Supervision time= Poll Rate + Ack Wait + [(Ack Wait) x (Retry Count)]
    Example:
    Poll =210
    Ack=15
    Retry Count=5
         Supervision time = 210 + 15 + (5 x 15) = 300 seconds
                                      or 225 + 75 = 300seconds

    Icon--AD-black-48x48Icon--address-consumer-data-black-48x48Icon--appointment-black-48x48Icon--back-left-black-48x48Icon--calendar-black-48x48Icon--center-alignedIcon--Checkbox-checkIcon--clock-black-48x48Icon--close-black-48x48Icon--compare-black-48x48Icon--confirmation-black-48x48Icon--dealer-details-black-48x48Icon--delete-black-48x48Icon--delivery-black-48x48Icon--down-black-48x48Icon--download-black-48x48Ic-OverlayAlertIcon--externallink-black-48x48Icon-Filledforward-right_adjustedIcon--grid-view-black-48x48IC_gd_Check-Circle170821_Icons_Community170823_Bosch_Icons170823_Bosch_Icons170821_Icons_CommunityIC-logout170821_Icons_Community170825_Bosch_Icons170821_Icons_CommunityIC-shopping-cart2170821_Icons_CommunityIC-upIC_UserIcon--imageIcon--info-i-black-48x48Icon--left-alignedIcon--Less-minimize-black-48x48Icon-FilledIcon--List-Check-grennIcon--List-Check-blackIcon--List-Cross-blackIcon--list-view-mobile-black-48x48Icon--list-view-black-48x48Icon--More-Maximize-black-48x48Icon--my-product-black-48x48Icon--newsletter-black-48x48Icon--payment-black-48x48Icon--print-black-48x48Icon--promotion-black-48x48Icon--registration-black-48x48Icon--Reset-black-48x48Icon--right-alignedshare-circle1Icon--share-black-48x48Icon--shopping-bag-black-48x48Icon-shopping-cartIcon--start-play-black-48x48Icon--store-locator-black-48x48Ic-OverlayAlertIcon--summary-black-48x48tumblrIcon-FilledvineIc-OverlayAlertwhishlist