When connected to the SDI bus, the B426, B420 or DX4020 is addressed as SDI 88 or SDI 92. Refer to the device installation guide for address configuration.
Device Message Failing to Poll on:
SDI88 Comm Trouble / Fail SDI 88 Address 88, Path 1
SDI88 Comm Trouble / Fail SDI 89 Address 88, Path 2
SDI88 Comm Trouble / Fail SDI 90 Address 88, Path 3
SDI88 Comm Trouble / Fail SDI 91 Address 88, Path 4
SDI92 Comm Trouble / Fail SDI 92 Address 92, Path 1
SDI92 Comm Trouble / Fail SDI 93 Address 92, Path 2
SDI92 Comm Trouble / Fail SDI 94 Address 92, Path 3
SDI92 Comm Trouble / Fail SDI 95 Address 92, Path 4
2. Network interface when used on the SDI bus:
When connected to the SDI 2 bus, the B426, B420 or DX4020 is addressed as 1 or 2. Refer to the device installation guide for address configuration.
Device-Addr Message Failing to Poll on:
SDI2-1 Comm Trouble / Fail SDI 11 Path 1, Address 1
SDI2-1 Comm Trouble / Fail SDI 21 Path 2, Address 1
SDI2-1 Comm Trouble / Fail SDI 31 Path 3, Address 1
SDI2-1 Comm Trouble / Fail SDI 41 Path 4, Address 1
SDI2-2 Comm Trouble / Fail SDI 12 Path 1, Address 2
SDI2-2 Comm Trouble / Fail SDI 22 Path 2, Address 2
SDI2-2 Comm Trouble / Fail SDI 32 Path 3, Address 2
SDI2-2 Comm Trouble / Fail SDI 42 Path 4, Address 2
3. New G Series (B8512G/B9512G) and B Series panels using Onboard Ethernet or Cellular:
Panels using Onboard IP or Plug-in Cellular will display the path number followed by device address 0.
Device Message Failing to Poll on:
Onboard Ethernet Comm Trouble SDI 10 Path 1, Address 0
Onboard Ethernet Comm Trouble SDI 20 Path 2, Address 0
Onboard Ethernet Comm Trouble SDI 30 Path 3, Address 0
Onboard Ethernet Comm Trouble SDI 40 Path 4, Address 0
Onboard Cellular Comm Trouble SDI 18 Path 1, Address 8
Onboard Cellular Comm Trouble SDI 28 Path 2, Address 8
Onboard Cellular Comm Trouble SDI 38 Path 3, Address 8
Onboard Cellular Comm Trouble SDI 48 Path 4, Address 8