When two Popits are addressed with the same dip-switch setting, the panel sees the address as Faulted regardless that an end-of-line resistor is connected across the loop input. Use the following steps to troubleshoot.
- Verify the point is programmed with the correct Point Source.
- Select Popex for points using the B299 interface.
- Select Zonex if using the D8125 interface .
- Change the popit dip-switch address by temporarily flipping the 0 switch. If the 0 switch is on, turn it off or vice versa. Alternatively, disconnect the correctly addressed popit and reconnect the Zonex loop wires to continue the loop.
- Use View Point Status to check the state of the point (see the article; How to use View Point Status).
- If the point state changed from Faulted to Normal, then there is another popit in the system with the same address as the one which was disconnected.
- If the point state changed from Faulted to Missing, then another issue in the loop is causing the disconnected point to go missing. See How to troubleshoot popit loops.
- Isolate the duplicate addressed popit by half splitting the popit loop until the duplicate address goes missing. Continue half splitting to isolate the errant popit.