The 4412 and the 6412 swinger shunt is set to 1 by default. This feature allows the automatic bypass of points. If the swinger bypass is selected yes in the point index that is assigned to the point, and the point goes into alarm or trouble more times than the swinger count is set at in one arming cycle, when the counter reaches 0 in 1 arming period, the alarm output and reporting can be disabled. Example. If I set the swinger count to 1 and there is one alarm in a single arming period, the counter will reach 0 and the point if programmed can be bypassed. The counter is reset every time the system is armed and disarmed. The actual counter can be changed in programming.
To change the programming for the alarm output swinger, from keypad programming:
1. nibble 1029 default is 1, 0=disabled and can be 1-15
a. to access this nibble, press 1029 then the command key, enter the value you wish to change it to and press the * key.
To change the programming for the point reports swinger, from keypad programming:
2. nibble 1030 default is 1, 0= disabled and can be 1-15.
a. to access this nibble, press 1030 then the command key, enter the value you wish to change it to and press the * key.
Exit programming and retest the system to verify the changes took effect.
... View more