Issue - What effect does alarm verification have on the point? Solution - When an Alarm Verification point enters into alarm, the control panel removes power from all Resettable points for the duration programmed in A# Verify Time. When power is reapplied, a 60-second confirmation window begins. If the detector is still in alarm and experiences another alarm during the confirmation window, or a different Resettable Verification point in the area sense a alarm, an alarm occurs. Program Point Index: Fire Point, Alarm Verify, and Resettable to YES. Program A# Alarm Verify: The default of 60 seconds meets UL 864 4th edition requirements. Use Alarm Verify with fire points only. During Fire Walk test, the reset time is 5 seconds. The Reset Sensors time (CMD 47) converts from the 5 second default time to the time programmed in A# Verify Time when a point programmed for P## Alarm Verify enters into alarm condition. Unverified Event report is not related to A# Verify Time. Unverified events are for cross points. Do not enable Cross Point if Alarm Verify is enabled. Part numbers D7212,D7412, D9112, D9124, D9412, D7212G,D7412G, D9112G, D9124G, D9412G, D7212GV2,D7412GV2, D9124GV2, D9412GV2, D7412GV3, D9412GV3, D7412GV4, D9412GV4, B8512G, B9512G