Step-by-step guide:
1. Determine which type of FPD-7024 hardware in use. There are differences in network communications programming depending on which type is in use (see figure 1).
- Version 1.00-1.03 panel types are identified with words on panel keypads instead of Icons.
- Version 1.06+ panel types are identified with Icons on panel keypads instead of words.
2. Obtain the following parameters.
- Receiver IP Address and Port number.
- Panel account number.
- Supervision interval configured in central station’s network account for the panel.
3. The Number entry combines the receiver IP address and network supervision into a single location
4. Using the programming menu tree in figure 3 as a guide, follow the steps below to configure network communications in the version 1.03 or 1.06 panel type.
Keypad Programming using menu tree
- Press 0 followed by the installer code (default= 9876) to access keypad programming.
- Save entries by pressing [ # ], or press star [ * ] to go back one level. Continue pressing star [ * ] to exit programing.
5. Determine the number entry according to the panel type in use.
- Version 1.03 and earlier.
- Use 300 second supervision both in the panel configuration as well as the network account at central station.
- 300 second supervision= Ack=15seconds, Poll=180 seconds and communication attempts=5 (the number of communication attempts is entered in a later step).
- Combine the IP address and network supervision as described in table 1.
- For example, enter the receiver IP address; 1 7 3. 8 4. 3 3. 8 2 as described in figure 4.
- Version 1.06 and newer.
- Determine the network supervision to be used in the panel and in central station’s network account (up to 24hours).
- Combine the IP address and network supervision as described in table 2. The number of communication attempts is entered in a later step.
- For example, enter the receiver IP address; 1 7 3. 8 4. 3 3. 8 2 using 24-hour supervision as described in figure 5.
6. Enter the receiver IP address and supervision interval.
- Press 6-Program Accounts.
- Press 1-PHONE/IP# 1.
- Press 1-Number.
- Enter the number from step 1.
- Press # to save.
7. Enter the receiver Port number.
- Press 2-PORT NUMBER.
- Enter the receiver port number. For example, Port 7700 is entered as 07700.
- Press # to save.
8. Enter the panel reporting format.
- Press 3-FORMAT. Select a reporting format and press # to save.
- 0- DISABLE
- 1- 3/1 REPORT
- 2- 4/2 REPORT
- 3- BFSK REPORT
- 4- SIA, 110 RPRT
- 5- CONTACT ID
- 6- SIA, 300 RPRT
- 7- MDM 3A2 (Modem)
9. Enter the panel account number.
- Press 4-ACCT NUMS.
- Ver. 1.03 and earlier: Enter the 4-digit account number and press # to save.
- Ver. 1.06 and newer: Enter the account number with leading zero’s, e.g. 0000001234 to fill all 10 digits.
10. **Version 1.06 only** Select IP MOD Primary.
- Select 1 or 2 as described below for the address of the primary network communicator. This applies only when there are 2 communicators used for network communications. Note that only the
- 1-250 as Primary
- 2-134 as Primary
- When a single network communicator is used, select 1 and address the communicator as 9 (option bus address 250).
- When a second network communicator is used, address the secondary communicator as 6 (option bus address 134).