    How to use keypad programming to configure FPD-7024 IP communications?

    Step-by-step guide:

     

    1. Determine which type of FPD-7024 hardware in use. There are differences in network communications programming depending on which type is in use (see figure 1).

    • Version 1.00-1.03 panel types are identified with words on panel keypads instead of Icons.
    • Version 1.06+ panel types are identified with Icons on panel keypads instead of words.
    Central_Support_0-1662562197071.png

     

    2. Obtain the following parameters.

    • Receiver IP Address and Port number.
    • Panel account number.
    • Supervision interval configured in central station’s network account for the panel.

     

    3. The Number entry combines the receiver IP address and network supervision into a single location

    Central_Support_2-1662562271900.png

     

    4. Using the programming menu tree in figure 3 as a guide, follow the steps below to configure network communications in the version 1.03 or 1.06 panel type.
    Keypad Programming using menu tree

    Central_Support_3-1662562326210.png
    • Press 0 followed by the installer code (default= 9876) to access keypad programming.
    • Save entries by pressing [ # ], or press star [ * ] to go back one level. Continue pressing star [ * ]  to exit programing.

    5. Determine the number entry according to the panel type in use.

    • Version 1.03 and earlier.
      • Use 300 second supervision both in the panel configuration as well as the network account at central station.
      • 300 second supervision= Ack=15seconds, Poll=180 seconds and communication attempts=5 (the number of communication attempts is entered in a later step).
      • Combine the IP address and network supervision as described in table 1.
    Central_Support_4-1662562391967.png

     

    • For example, enter the receiver IP address; 1 7 3. 8 4. 3 3. 8 2 as described in figure 4.
    Central_Support_5-1662562447522.png

     

    • Version 1.06 and newer.
      • Determine the network supervision to be used in the panel and in central station’s network account (up to 24hours).
      • Combine the IP address and network supervision as described in table 2. The number of communication attempts is entered in a later step.
        Central_Support_7-1662562545329.png

         

      • For example, enter the receiver IP address; 1 7 3. 8 4. 3 3. 8 2 using 24-hour supervision as described in figure 5.
     
    Central_Support_8-1662562604876.png

     

    6. Enter the receiver IP address and supervision interval.

    • Press 6-Program Accounts.
    • Press 1-PHONE/IP# 1.
    • Press 1-Number.
    • Enter the number from step 1.
    • Press # to save.

    7. Enter the receiver Port number.

    • Press 2-PORT NUMBER.
      • Enter the receiver port number. For example, Port 7700 is entered as 07700.
      • Press # to save.


    8. Enter the panel reporting format.

    • Press 3-FORMAT. Select a reporting format and press # to save.
      • 0- DISABLE
      • 1- 3/1 REPORT
      • 2- 4/2 REPORT
      • 3- BFSK REPORT
      • 4- SIA, 110 RPRT
      • 5- CONTACT ID
      • 6- SIA, 300 RPRT
      • 7- MDM 3A2 (Modem)

    9. Enter the panel account number.

    • Press 4-ACCT NUMS.
      • Ver. 1.03 and earlier: Enter the 4-digit account number and press # to save.
      • Ver. 1.06 and newer: Enter the account number with leading zero’s, e.g. 0000001234 to fill all 10 digits.

    10. **Version 1.06 only**  Select IP MOD Primary.

    • Select 1 or 2 as described below for the address of the primary network communicator. This applies only when there are 2 communicators used for network communications. Note that only the
      • 1-250 as Primary
      • 2-134 as Primary
    • When a single network communicator is used, select 1 and address the communicator as 9 (option bus address 250).
    • When a second network communicator is used, address the secondary communicator as 6 (option bus address 134).
    Version history
    Last update:
    ‎09-07-2022 05:00 PM
    Updated by:
    Contributors
    Icon--AD-black-48x48Icon--address-consumer-data-black-48x48Icon--appointment-black-48x48Icon--back-left-black-48x48Icon--calendar-black-48x48Icon--center-alignedIcon--Checkbox-checkIcon--clock-black-48x48Icon--close-black-48x48Icon--compare-black-48x48Icon--confirmation-black-48x48Icon--dealer-details-black-48x48Icon--delete-black-48x48Icon--delivery-black-48x48Icon--down-black-48x48Icon--download-black-48x48Ic-OverlayAlertIcon--externallink-black-48x48Icon-Filledforward-right_adjustedIcon--grid-view-black-48x48IC_gd_Check-Circle170821_Icons_Community170823_Bosch_Icons170823_Bosch_Icons170821_Icons_CommunityIC-logout170821_Icons_Community170825_Bosch_Icons170821_Icons_CommunityIC-shopping-cart2170821_Icons_CommunityIC-upIC_UserIcon--imageIcon--info-i-black-48x48Icon--left-alignedIcon--Less-minimize-black-48x48Icon-FilledIcon--List-Check-grennIcon--List-Check-blackIcon--List-Cross-blackIcon--list-view-mobile-black-48x48Icon--list-view-black-48x48Icon--More-Maximize-black-48x48Icon--my-product-black-48x48Icon--newsletter-black-48x48Icon--payment-black-48x48Icon--print-black-48x48Icon--promotion-black-48x48Icon--registration-black-48x48Icon--Reset-black-48x48Icon--right-alignedshare-circle1Icon--share-black-48x48Icon--shopping-bag-black-48x48Icon-shopping-cartIcon--start-play-black-48x48Icon--store-locator-black-48x48Ic-OverlayAlertIcon--summary-black-48x48tumblrIcon-FilledvineIc-OverlayAlertwhishlist