Issue
Can 40 be used as the first address for a D7052 Dual Point Module or D7053 I/O Module?
Solution
The first address on the I/O module can not be set to a multiple of 8. As a rule of thumb, set the first address as an odd number and you will never hit a multiple of eight.
Addresses that cannot be used to start with on a D7052, D7053, or D7042:
Mux Bus A
16,32,40,48,56,64,72,80,88,96,104,112,120,128
Mux Bus B (if Wired Class B)
136,144,152,160,168,176,184,192,200,208,216,224,232,240,248
Part numbers D7024, FPD-7024, D7042, D7052, D7053
... View more