Issue
The Timer Test is not coming in. The panel history shows Off Normal Test. The panel is programmed to send all reports in CID. Central does not see an E608 CID report for an off normal test.
Solution
Contact ID Reporting. The system can be programmed to send a periodic test report, E602, in Contact ID format. If any system troubles are present at the periodic test time, a new event, E608, which states “New event, off normal at time of periodic test report” is sent. Software versions 2.03 and before sent a generic system trouble P300 report.
Part numbers DS9400, DS9400I, DS9400M, DS9431, D7024
Issue
Control trouble # 87 displays Battery Trouble.
Probable Cause:
The battery failed a battery test
The battery is defective
The wiring to the battery is disconnected
Solution:
If there has just been a power failure, wait a least 24 hours for the battery to recharge, then perform a system reset to re-test the battery and clear the error
Replace the battery.
Check wiring.