Question:
Can an input device on one loop card trip an output device on a different loop card or network analog panel?
Answer:
Yes, it is possible to map an input device of one loop card to trip an output device on the same or different loop card on the same networked analog system.
Instructions on how to program the outputs below.
Zone mapping The control panel supports a flexible system to map input points to outputs. The system defaults so that all NAC outputs are activated by a fire alarm. By programming output zones, you can create almost any output activation scheme, such as "floor above and floor below" activation or conditional elevator recall. Input points: Smoke detectors, pull stations, and so on Zone: A group of input points (zones 1 to 225 are configurable, 226 to 234 are activated automatically) Outputs: Notification Appliance Circuits (NACs) such as bells, strobes, and relays Zone mapping on a networked system: – For each panel on the network there are 128 local zones (pp-001 to pp-128, where pp = the panel ID). Local zones are used to assign inputs and outputs specific to a device at that zone address and to that panel. – Each network also has 97 grouped zones (129 to 225). Grouped zone addresses allow inputs and outputs to be assigned to multiple panels within a network so that the inputs and outputs of each panel in the grouped zone can be connected to any of the panels in the network. – Each network also has 9 global zones (226 to 234). Global zones have preset inputs based on device types, but their outputs can be defined and apply to the entire network. – For local zones and group zones, up to 5 zones per input and 5 zones per output can be mapped. More specifically, an input can be mapped to local zones on any panel within the network or to group zones. The outputs from a local zone (1-128) can be mapped only to the panel that zone is connected to, but the output from group zones (129-225) can be mapped to any panel within the network. Mapping principles:
– Inputs activate zones, and zones activate outputs. – Input points can be assigned to up to five local or group zones. Therefore, each input can activate up to five zones; however, any number of inputs can be mapped to the same zone. – Up to five local, group, and/or global zones can be assigned to each output (except the FAA‑325‑B6S Analog Sounder Base which can be assigned to only one zone). – Zones 1 to 225 are available for the installer to program. – Zones 226 to 234 are global zones and are hard-coded to pre-assigned conditions. They are automatically activated by inputs if a special condition occurs or the panel is in a processing sequence (See the following two figures). It is not possible to assign an input point to any global zone. – An output can be assigned to a global zone so that it will be activated upon the corresponding special condition. For example, any input that is configured as a "Fire Auto" type activates Zone 226 when it is alarmed. Any output driven by Zone 226 activates when any “Fire Auto” type point is alarmed. For how inputs control zones and zones control outputs in a network, see the following figure.
Network input-output mapping
For how inputs control zones and zones control outputs in a stand-alone panel, see the following figure.
Stand-alone panel zone mapping
For a list of all global zones on the panel (each has a unique number), see the following table. Global Zone Number Condition Activating Zone
Pre-assigned zones 226 Global fire alarm 227 Global trouble 228 Global supervisory 229 Alarm verification (verification period) 230 Pre-signal (waiting for reset) 231 Positive Alarm Sequence (waiting for ACK or reset) 232 Panel is resetting 233 Global gas alarm 234 Global waterflow In some cases if a relay output is assigned to a certain global zone, other assigned zones are ignored: – Mainboard relay 1: If assigned to the global alarm zone, other assigned zones are ignored. The relay reacts only to the global alarm zone. – Mainboard relay 2: If assigned to the global trouble zone, other assigned zones are ignored. The relay reacts only to the global trouble zone. – Mainboard relay 3: If assigned to the global supervisory zone, other assigned zones are ignored. The relay reacts only to the global supervisory zone. Outputs is active if any zone to which the output is assigned is activated. An output which is assigned to multiple zones can be considered as inactive only when all associated zones are inactive. NAC pattern assignment Every zone is assigned to one NAC pattern. When the zone NAC pattern is set to default, the device NAC pattern is used. In case of a device activation by address, the device NAC pattern is used. When a device is activated by a zone activation command, the NAC activates with the assigned zone pattern (Steady, Pulsing, or Temporal Code 3, for global gas alarm also Temporal Code 4). See the following table.
NAC pattern assignment
Counting zones All local or group zones have the “Counting Zones” option. If this option is enabled, a local or group zone becomes a counting zone. Otherwise, it is a non-counting zone which is activated as soon as an input point assigned to this zone is activated. If multiple points (can be from different panels if networked) are assigned to a single zone, only when all the points are inactive is the zone considered as inactive; thus, associated outputs can be deactivated. A counting zone is considered active only when two or more input points assigned to that zone are active. It is not allowed to assign an input point programmed with any delayed point features (including PAS, Pre-signal, alarm verification, and PAS@day or alarmverification@night) to a counting zone.