Issue
The D192G panel zone (point) is in trouble and the yellow LED is not on.
Solution
With the zone/point in trouble and No Yellow LED On there is a wiring fault. One of the following terminals do not have power connected to them. External Power In (EXT PWR IN) and / or Auxiliary Power In (AUX PWR IN).
Terminal 1 (AUX PWR IN) 13.75 VDC
Terminal 2 (Common)
Terminal 3 (Supervised Zone / Point) 2.50 VDC Normal Condition < 1.50 VDC In Trouble condition
Terminal 4 (Trigger) 13.75 VDC In Alarm Only
Terminal 5 (External Power In) 12 VDC or 24 VDC Depended on needed Output for the NAC's or Power Supply
Terminal 6 (Common) This is the Common from an 24 VDC External Power
Terminal 7 (Positive Alarm Output)
Terminal 8 (Negative Alarm Output)
Part number D192G
Issue
Does the D7038 have built in Sync?
Solution
No, the Sync module is needed. The D7038 Input will pass the Sync Pulse to each Output.
Sync Module Part Numbers
Brand Name Sync Module Part Number
System Sensor MDL
Wheelock DSM; SM
Gentex AVS44; AVSM
Note: If the DS9400 Series or D7024 Series panel is used with the D7038, NAC's 1 or 2 on the D7024 or DS9400 can provide a Wheelock Sync pulse. If the Eprom Revision is 2.04 or higher, either panel series can also provide a Gentex Sync Pulse from NAC 1 and or NAC 2.
Part numbers DS9400, DS9400I, DS9400M , D7024, DS9484, D7038
The D9124 is a 9000 control panel with a 24Vdc PSU and all the needed Fire Accessories for a basic system, all in one large red enclosure. See parts List below.
The D9124 is made up of the following:
D9112LTB, D9412LTB ,D9412GLTB, D9412GV2LTB - Control Panel
D9101 - Red Enclosure
D9100 - Carriers Module with the Following parts *
* 2 - D192C - Bell Supervision Modules
* 1 - D8125 - Popex Module
* 1 - D928 - Dual Phone line Switcher
* 1 - D9142LC - 24Vdc Power Supply
D1256 - Fire Keypad
D1601 - Hardwire Transformer
Issue
D8112 Displays CPU FAIL.
Solution
D8112 Displays CPU FAIL
Remove Data wires from terminals 30 and 31.
Copy the panel via RAMii, RPS or D5200 and save the copy.
Send the panel a NEW RECORD or Blank Account. (Basically set the panel back to factory default.)
Reload the regional copy back in the panel.
Reattach the Data wires to terminals 30 and 31.
If still in CPU FAIL - Rewrite the saved copy of the program and save as a different file name.
Remove Data wires from terminals 30 and 31.
Send the panel a NEW RECORD or Blank Account.
Send the new file into the panel.
Reattach the Data wires to terminals 30 and 31.
If still in CPU FAIL - replace the panel.