This article explains is we can use Remote desktop to run or use the FSM client.
When using remote desktop the error below will be shown when remote desktop is minimized and then maximized, the only option is to close the FSM client and start again.
To silence all NAC's of one panel (FPA-5000/Avenar) from the map in FSM
Step-by-step guide
Insert a sensor on the map of FSM
Under sensor properties choose:
General:
Add symbol: FIRE_Panel_FPA_BG
Settings:
Driver Instance: the panel / compound where the FSM is belongs to
Address-> e.g. Panel 1-10.1
! Please pay attention: there are other “Panel” possibilities to choose. Please do not choose Panel 1-10 (Communication)!
After inserting the settings click “ok”
Then Apply
At the map when you right click the panel symbol you will get the commands as shown below.
If there is a fire alarm, you can right click at the panel and then click at “silence on”.
Please be sure, that then every NAC which is belonging to this panel is “silenced”.
Additional: there is also a command "silence scope" which then has the effect, that the whole scope will be silenced.