Question
The central station received a message of No Acknowledgement Received, which may have been shown as X71 in 6500 mode or NYU0001 in SIA mode. What causes this problem with the C900TTL-E or C900V2 module?
Answer
The message indicates that the C900 module relayed the message to the central station receiver, but the panel has not responded to the acknowledgement request (kissoff).
Check the dip-switch settings for the communication format.
Verify the communication format is correct on the C900, and the same communication format is selected in the panel.
Verify that the C900 firmware version is compatible with the selected communication format (see C900 module's installation manual for a compatibility list).
Check the panel itself for a potential issue, such as a phone cable, ground fault, or power problem.
Verify that the C900 module is getting minimum voltage required, 12 to 24 volts DC.
Ensure that the power supply for the C900 is a dedicated source of filtered DC voltage, and it can supply enough current for the C900 module (~280mA).