Washer trigger is not working for MIC-7522-Z30W (MIC IP starlight 7100i)
MIC-7522-Z30W camera is connected with MIC-ALM-WAS-24 interface module using RS485 communication.
When trying to trigger the washer unit from the camera, it is not responding.
First step in the camera config is to check if you have selected the right Application Variant:
Make sure that the red button test is successful:
Please note that the relay output of the IO Alarm card is a dry contact relay (with 24VAC/VDC, 5 A). In order to control another circuit that has a 230V you can't do that directly because its higher than it was design for. In order to safety control a 230V, you could use a 24V on that output and control an additional/external relay: powering its coil this relay could switch the 230 circuit of the washer.
See attached schematic:
After taking into consideration the above, the washer pump should work as expected when you manually trigger the relay.
After checking the Application Variant and after consulting the Installation Manual of MIC-ALM-WAS-24 (MIC Alarm‑Washer Box), make sure that:
Nice to know: