When programming the FPD-7024 Fire Control Panel from RPS, the first character of the Phone number or IP Address is not always programmed. You need to verify the panel program by hand from the panel keypad.
When programming a phone number it must start 1 then > (wait dial tone symbol), then the Central Station phone number. Example 1>18002890096.
If programming an IP address see below for each firmware type.
Firmware 1.03 and older with 5 Minute Supervision - Enter 0 to tell the panel this is an IP Address (then enter the 12 digit IP Address of the Central Station) followed by 015 the ACK Wait time then 150 the Poll Rate time then 1 Enable Anti-replay follow by # Enter (Refer to the below)
Firmware 1.06 and higher with 5 Minute Supervision - Enter 0 to tell the panel this is an IP Address (then enter the 12 digit IP Address of the Central Station) followed by 015 the ACK Wait time then 180 the Poll Rate time then 1 Enable Anti-replay follow by 0 ACK Time interval (0 = Seconds, 1 = Minutes, 3 = Hours) follow by 0 Heartbeat Time interval (0 = Seconds, 1 = Minutes, 3 = Hours) then # Enter (Refer to the chart below).