The programmer for the DACT family (D9068,FPT-DACT; DCT-1; DCT-1E; DS9602) is one of the following: D7033 DS9447 FMR-DACT-KEYPAD Notes The FMR-DACT-KEYPAD is not the same as the FMR-7033. The FMR-7033 will not program the D9068 DACT family (FPT-DACT; DCT-1; DCT-1E; DS9602).
Issue
The Timer Test is not coming in. The panel history shows Off Normal Test. The panel is programmed to send all reports in CID. Central does not see an E608 CID report for an off normal test.
Solution
Contact ID Reporting. The system can be programmed to send a periodic test report, E602, in Contact ID format. If any system troubles are present at the periodic test time, a new event, E608, which states “New event, off normal at time of periodic test report” is sent. Software versions 2.03 and before sent a generic system trouble P300 report.
Part numbers DS9400, DS9400I, DS9400M, DS9431, D7024
Perform these steps to enable the D7024, FPD-7024, DS9400, DS9400I, and DS9400M for RPS programming via phone line with a compatible RPS modem: Press (0) Enter Program Mode. Enter Pin (Default is 9876). Press (6) Accounts. Press (4) Ring Count. Set Ring Count to (02) #. Press the (*) key two times or until you see PROGRAM MODES. Press (3) System. Press (7) Remote Program. Press (1) Enable. Press the (*) key five times to Exit Program Mode. You need to dial Line 1 on the panel. It is the second line down on the panel (it is NOT the line in the top right). Before connecting with RPS, perform an Auto-Learn with at least one Mux Device connected to the Mux loop, then send your RPS program to the panel. Press (0) Enter Program Mode. Enter Pin (default is 9876). Press (9) Program Mux. Press (4) Auto Program. Press (1) Yes.
Issue
D8112 Displays CPU FAIL.
Solution
D8112 Displays CPU FAIL
Remove Data wires from terminals 30 and 31.
Copy the panel via RAMii, RPS or D5200 and save the copy.
Send the panel a NEW RECORD or Blank Account. (Basically set the panel back to factory default.)
Reload the regional copy back in the panel.
Reattach the Data wires to terminals 30 and 31.
If still in CPU FAIL - Rewrite the saved copy of the program and save as a different file name.
Remove Data wires from terminals 30 and 31.
Send the panel a NEW RECORD or Blank Account.
Send the new file into the panel.
Reattach the Data wires to terminals 30 and 31.
If still in CPU FAIL - replace the panel.