When using Wheelock / Cooper / Eaton Exceeder LED 3 Strobes and Horn Strobes on a UL Listed Bosch Fire panel a DSM or SM Wheelock Sync Module is required.
The controller is showing faults but when you access the faults option no errors/fault messages are shown, message 'no suitable element' is shown. Why?
This is how to troubleshoot where turning the key to the Test position does not put the smoke detector inside the duct enclosure into alarm, which will likely be due to the coil is missing.
The operator 10000 is shown when detector fault/ Fire is acknowledged on the controller when no operator is logged in (e.g. Operator 2), by pressing the Acknowledge button.
With FSM 5.6 the database.xml structure was slightly changed and FSM 5.6 is supporting only the new database.xml structure.
This is leading after upgrade to a loss of the configured symbols (only the symbols, not the content of the devices configured on the floor plans).
Therefore after upgrading from older FSM version (e.g. 5.2) to 5.6, the already configured symbols of sensors on maps are not shown correctly, they are shown are dots/circles.
Please note: If before executing the file provided below the application was opened and the sensor properties were edited by approving > at that step the symbols changed to the default symbol and the previously configured symbol cannot be recovered.