*New Feature - Summary Fire Relay Option - GV2 Firmware 7.05 An option is added that changes the duration of the Panel Wide Summary Fire Relay output. Select GV2AUX→MISCELLANEOUS→Fire Summary Sustain: Yes: Summary Fire Relay clears when all Fire Alarms are cleared from the display. No: Summary Fire Relay clears when the area FireAlarms are silenced and all area Fire Points return to normal. The default option is No. This feature provides a way to maintain the fire strobes active after the alarm bell outputs are silenced.
Part numbersD7412GV2, D7412GV2, D9412GV2, D7212GV3, D7412GV3, D9412GV3, D7412GV4, D9412GV4, B8512G, B9512G
Issue - Can the MUX data loop be run in the same cable of wire as the Keypad data wires? Solution - They cannot, they are two different data outputs. They should never be run in the same jacketed of wire. They each require their own wire run and should at least 3 inches apart in the raceway. Part numbers DS7400X, DS7400Xi, DS7400, DS7400XIVER3+, DS7400XIVER4+, DS7400XIVER2, DS7430, DS7436, DS7447