Can the D125B be Used to Power 2 Wire Smokes on the D7112?
Yes, see technogram number (73-06116-000-C) 1993 (attached). Listings and Approvals Underwriters Laboratories lists the D7112 ControVCommunicator as a Digital Alarm Communicator Transmitter (DACT) for: NFPA 71 Central Station, NFPA 72 Chapter 6 Local, NFPA 72 Chapter 8 Remote Station, NFPA 74 Household Fire Warning. The D7112 also has the following Approvals: CSFM and NYC-MEA (formerly NYC-BSA).
Issue
D7112 Panel battery will not hold a charge.
Solution
A slow flashing (1 sec on, 1 sec off) yellow LED with the green CPU LED off indicates a power supply overload condition. The panel detects the battery as missing and the power supply cannot meet the power demand of the devices on the panel. The panel is shut down.
How to correct the D132A supervision point not showing normal circuit status.
Cannot get the onboard point from the D132A module to show normal circuit status.
D132A,D4412,D6412,DS7220,DS7240,D2212
Issue
What is the force arm or bypass max on the DS7100?
Solution
The bypass max is only limited by point programming, if the point is programmed in data digit 3 as bypassable then it may be bypassed no matter how many other zones may also be bypassed while arming.