    Security: Intrusion

    Sort by:
    a week ago
    1 Select Panel Wide Parameters:   2 Under Panel Wide Parameters > Select Communicator:   3  Change your Primary Path Device to Cellular IP Path 1:   4 Next, go to Enhanced Communication:   5 Double-Click the Network address to input your Central Station Receiver’s IP address.   6 Set your Supervision Time. Note: this should also match what is in your central station receiver to eliminate erroneous communication trouble.   ⚠️   Be sure to notify you Central Station to add your area 1 account number, supervision rate and enable the receiver for Re-synchronization.
    View full article
    ‎04-06-2021 09:55 AM
    You can use the Advantech ADAM-4541 Fiber Optic Converter to connect SDI2 devices via fiber optic cabling. Using fiber optic cabling allows you to extend the distance between SDI2 devices. Do not include the length of the fiber cabling in your wire length calculations for the SDI2 bus. Building-to-building SDI2 connections of SDI2 devices such as keypads, access control modules, power supplies, wireless receivers, input modules, and output modules are easily made. Notice: Use of the Advantech ADAM-4541 Fiber Optic Converter and SDI2 devices has not been investigated by Underwriter’s Laboratories. Do not use for UL applications or applications that include fire alarm components.
    View full article
    ‎04-06-2021 09:53 AM
    If looking to apply power (complete the circuit): NO of the DS150 to the Positive of the Maglock. From the negative of the Maglock to the negative of the power supply. From the Positive of the power supply to Common on the DS150.   If looking to remove power (break the circuit): NC of the DS150 to the Positive of the Maglock. From the negative of the Maglock to the negative of the power supply. From the Positive of the power supply to Common on the DS150.   Note: Generally we do fail safe not fail secure and the relay timer needs to be incremented.
    View full article
    ‎04-06-2021 09:52 AM
    Output A can be configured as a Form C, Com reference or as a Dry contact depending on how you put the jumper under the panel cover. This article will help you to find out how you can configure output A (1) on the B Series Panel.
    View full article
    ‎04-06-2021 09:51 AM
    Test Reports can be set up from Teraterm or RPS (requires firmware 2.0 or above). The test report timer (re)starts when the panel item is changed or when the module reboots, once the timer expires the test report is sent. Step-by-step guide   Teraterm/RPS: Go to System Configuration > Test Report Settings > Test Report Interval The timer options are  Off, 4hr, 6hr, 12hr, or 24h
    View full article
    ‎04-06-2021 09:47 AM
    How to configure the output in GV4 ver.2? Default: 0 Selections: 0 to 8 (increments of 1) Use this parameter to activate an output when the point goes into alarm. The output does not activate for Trouble nor Supervisory events. Reset the output by clearing the memory from the keypad display. The outputs used can be on an output module installed on either the Zonex bus or the SDI2 bus.   *Notice that the   Relay will activate only when the point goes in to alarm,   not when it changes to an off-normal state. Follow the steps from this article to accomplish the BFSK relay functionality.
    View full article
    ‎04-06-2021 09:32 AM
    For Normally Closed (NC) circuits, wire the resistor in series with the circuit For Normally Open (NO) circuits, wire the resistor in parallel with the circuit
    View full article
    ‎04-06-2021 09:31 AM
    If there is no G in the panel's name, there is no ground fault detection and the panel does not have an S4 pin. If it has a single G in the name it has the chance it could be enabled if S4 is latched and under area 5 silent alarm relay there is a value other than 0. If it’s a GV2, GV3 or GV4 and S4 is latched, ground fault detection is enabled. If there is ground fault detection, latch S4 and measure DC voltage on Terminals 9 and 10: You should get 6.5-6.8 VDC Steady (not jumping around) when there isn't a ground fault. If there is a ground fault it can take up to a minute to display and clear at the keypad.
    View full article
    Icon--AD-black-48x48Icon--address-consumer-data-black-48x48Icon--appointment-black-48x48Icon--back-left-black-48x48Icon--calendar-black-48x48Icon--center-alignedIcon--Checkbox-checkIcon--clock-black-48x48Icon--close-black-48x48Icon--compare-black-48x48Icon--confirmation-black-48x48Icon--dealer-details-black-48x48Icon--delete-black-48x48Icon--delivery-black-48x48Icon--down-black-48x48Icon--download-black-48x48Ic-OverlayAlertIcon--externallink-black-48x48Icon-Filledforward-right_adjustedIcon--grid-view-black-48x48IC_gd_Check-Circle170821_Icons_Community170823_Bosch_Icons170823_Bosch_Icons170821_Icons_CommunityIC-logout170821_Icons_Community170825_Bosch_Icons170821_Icons_CommunityIC-shopping-cart2170821_Icons_CommunityIC-upIC_UserIcon--imageIcon--info-i-black-48x48Icon--left-alignedIcon--Less-minimize-black-48x48Icon-FilledIcon--List-Check-grennIcon--List-Check-blackIcon--List-Cross-blackIcon--list-view-mobile-black-48x48Icon--list-view-black-48x48Icon--More-Maximize-black-48x48Icon--my-product-black-48x48Icon--newsletter-black-48x48Icon--payment-black-48x48Icon--print-black-48x48Icon--promotion-black-48x48Icon--registration-black-48x48Icon--Reset-black-48x48Icon--right-alignedshare-circle1Icon--share-black-48x48Icon--shopping-bag-black-48x48Icon-shopping-cartIcon--start-play-black-48x48Icon--store-locator-black-48x48Ic-OverlayAlertIcon--summary-black-48x48tumblrIcon-FilledvineIc-OverlayAlertwhishlist