This website uses absolutely necessary cookies. If you consent to the use of convenience cookies, please click “Yes, I agree.” By clicking on “Privacy Settings.” you can change this setting at any time and withdraw your given consent. Icon down see more You can find detailled information in our Privacy Policy Icon forward-right
Icon up see less

Bosch Building Technologies

    cancel
    Showing results for 
    Search instead for 
    Did you mean: 

    Security: Intrusion

    Sort by:
    ‎07-30-2018 07:43 PM
    Issue How many 2 wire smokes will the D7112 support on zone 1?   Solution   Manufacturer & Models, and the number of smokes Radionics D262 with the D260 base  = 20 smokes DS200 with the MB200-2w base  = 10 smokes System Sensor 1400   =  10 smokes System Sensor 2400  = 10 smokes System Sensor 2400TH  = 10 smokes System Sensor 1451 with the B401 base  = 10 smokes System Sensor 1451 DH with the DH400 base  = 10 smokes System Sensor 2451 with the B401,B401B or DH400  = 10 smokes System Sensor 2451TH  with the B401,B401B or DH400  = 10 smokes System Sensor 2300T  = 10 smokes
    View full article
    ‎07-26-2018 05:03 PM
    What are the maximum number of 2 wire smokes that can be applied to loop B?
    View full article
    ‎07-26-2018 05:02 PM
    D462 Pull Stations - Do we make a plastic cover or tamper proof cover?
    View full article
    ‎07-11-2018 05:22 PM
    How is the D6112 panel set up to have a smoke detector reset for 4 wire smokes? D6112
    View full article
    ‎06-20-2018 06:35 PM
    D6412, D4412
    View full article
    ‎06-15-2018 06:13 PM
    Issue Can I mix Heat Detectors and 2 wire smokes with a sounder when using a D132A Smoke Detector Polarity Reversing Module? Solution No. When a Heat detector goes into alarm it puts a short on the input zone to indicate the alarm. The D132A uses Aux power from the panel when the polarity reversal takes place and since a heat detector does not reset when polarity is reversed, it would put a direct short on the Aux power of the panel. Consequently everything connected to the same Aux power terminals would not function.
    View full article
    ‎06-15-2018 02:07 PM
    How to configure the 2000 Series to use 4-Wire smokes. D2212,D2412,D2812 D133, D134
    View full article
    ‎06-06-2018 06:39 PM
    How to test the RF280THS wireless smoke used on the D4412 and D6412. When testing the RF280THS by pressing the 'Test' button does not generate a panel alarm.
    View full article
    Icon--AD-black-48x48Icon--address-consumer-data-black-48x48Icon--appointment-black-48x48Icon--back-left-black-48x48Icon--calendar-black-48x48Icon--center-alignedIcon--Checkbox-checkIcon--clock-black-48x48Icon--close-black-48x48Icon--compare-black-48x48Icon--confirmation-black-48x48Icon--dealer-details-black-48x48Icon--delete-black-48x48Icon--delivery-black-48x48Icon--down-black-48x48Icon--download-black-48x48Ic-OverlayAlertIcon--externallink-black-48x48Icon-Filledforward-right_adjustedIcon--grid-view-black-48x48IC_gd_Check-Circle170821_Icons_Community170823_Bosch_Icons170823_Bosch_Icons170821_Icons_CommunityIC-logout170821_Icons_Community170825_Bosch_Icons170821_Icons_CommunityIC-shopping-cart2170821_Icons_CommunityIC-upIC_UserIcon--imageIcon--info-i-black-48x48Icon--left-alignedIcon--Less-minimize-black-48x48Icon-FilledIcon--List-Check-grennIcon--List-Check-blackIcon--List-Cross-blackIcon--list-view-mobile-black-48x48Icon--list-view-black-48x48Icon--More-Maximize-black-48x48Icon--my-product-black-48x48Icon--newsletter-black-48x48Icon--payment-black-48x48Icon--print-black-48x48Icon--promotion-black-48x48Icon--registration-black-48x48Icon--Reset-black-48x48Icon--right-alignedshare-circle1Icon--share-black-48x48Icon--shopping-bag-black-48x48Icon-shopping-cartIcon--start-play-black-48x48Icon--store-locator-black-48x48Ic-OverlayAlertIcon--summary-black-48x48tumblrIcon-FilledvineIc-OverlayAlertwhishlist