Issue
The D8112 panel is not sending signals when modem format is selected to the Central Station.
Solution
Only the D8112G2 can send signals in Modem II format with a CS setting of 7.
The D8112E, D8112E1, D8112G, D8112G1 and D8112A must have CS set to either Blank or a selection between 1 and 6 but not 7.
Only Modem Format can report a 4 digit account number to the Central Station all others only report a 3 digit account number.
Issue
How many zones can be programmed on the D8112G2?
Solution
The D8112G2 is capable to have 8 master zones that may be expanded to 134 individual zones of protection.
Issue
How many Logger Events can the D8112G2 store?
Solution
The D8112G2 Control Communicator can store up to 400 Events in the panel memory. The panel logs the time, date, event, master zone, and the primary or alternate phone number called for each event. The 400 events can be retrieved with the RAM II, RAM IV or RPS downloading software.
Issue
What are the enviromental considerations for the proper operation of the Bosch control/communicators?
Solution
Indoor Dry.
Relative Humidity 5% to 85% noncondensing at +86 degrees Fahrenheit (+30 degrees Celsius).
Operating temperature would be +32 degrees Fahrenheit to +120 degrees Fahrenheit ( 0 degrees Celsius to 49 degrees Celsius ).
Issue
Why does the zone light on the D360 Command Center light when the D279A is disarmed?
Solution
The D8112 panel is programmed with a zone code of 3271 on a particular zone. The purple jumper on the D279A is cut. As a result, the D360 zone light illuminates when the D279A is disarmed.
This is normal and will not impact the D8112 arming process. If the D1252A is used, the disarm state of the D279A is not indicated.
How to correct the D8112/5505 not sending a Reboot report.
The 8112/5505 panel is communicating alarm and trouble signals but after resetting the panel it does not report the reboot.
5505,D8112A,D8112E1,D8112G1,D8112G2
How to control the D8112 buzz when test reports are sent.
The D8112 panel buzzes when it sends test reports, how can I stop the buzz?
D8112G2,D8112E1,D8112G1,D8112A
How to program the D8112 panel to report AC Restoral Reports.
Central Station Receiving AC Fail Reports but not AC Restoral Reports.
D8112E1,D8112G1,D8112A,D8112G2.