How to determine which control panel has SDI 92 available for the IP Communicator.
Which is the first panel that supported address 92 for communication devices on the SDI bus.
B420, B426, B450
Issue
Why does the zone light on the D360 Command Center light when the D279A is disarmed?
Solution
The D8112 panel is programmed with a zone code of 3271 on a particular zone. The purple jumper on the D279A is cut. As a result, the D360 zone light illuminates when the D279A is disarmed.
This is normal and will not impact the D8112 arming process. If the D1252A is used, the disarm state of the D279A is not indicated.
Does Max Number of B208 Limit the number of B308's that can be used?
Or,
Does Max Number of B308s Limit the number of B208 's that can be used?
No.
The maximum number of B208 modules and B308 modules that are available to the panel type can be connected at one time.
The only limit would be available power and SDI2 cable distance specifications which are detailed in the module documentation as well as the panel Installation and System Reference Guide (ISRG).
How to activate multiple auxiliary relays on Area Wide or Panel Wide Events.
Programming Area Wide or Panel Wide Relays will only allow a single relay entry. Use an auxiliary relay such as the D130, D133 or D134 when multiple relays are needed to energize on a panel event.
How to address SDI2 devices without causing address conflicts.
Can different types of SDI2 devices use the same address setting?
B810, RFRP-A, B820, B208, B308, B420, B426, B520, B920, B921C, B930, B942.