How to determine which control panel has SDI 92 available for the IP Communicator.
Which is the first panel that supported address 92 for communication devices on the SDI bus.
B420, B426, B450
Issue
When programming the D279 keypad point index on the 7000/9000, G, GV2, & GV3 series panels, how should the type and response be programmed?
Solution
Program a type 7 for D279 (O/C Non-Priority): The D279 provides point arming and disarming independent of the area arm state. A non-priority D279 point arm state does not affect the area arm state. Point Response must be programmed 1. Program type 8 for D279 (O/C Priority): The D279 provides point arming and disarming independent of the area arm state. A priority D279 point must be armed before an area can be armed. Program Point Response as 2.
Issue
How far can the D9131A be installed remoted from the control panel?
Solution
The D9131A can be installed a maximum of 1000 ft. (305m) from the panel using 22 AWG solid copper wire.
Does Max Number of B208 Limit the number of B308's that can be used?
Or,
Does Max Number of B308s Limit the number of B208 's that can be used?
No.
The maximum number of B208 modules and B308 modules that are available to the panel type can be connected at one time.
The only limit would be available power and SDI2 cable distance specifications which are detailed in the module documentation as well as the panel Installation and System Reference Guide (ISRG).