Bosch Building Technologies

    cancel
    Showing results for 
    Search instead for 
    Did you mean: 

    Security: Intrusion

    Sort by:
    ‎06-29-2018 08:33 PM
    How to correct the RS Control APP message:  "System is Disabled".
    View full article
    ‎06-29-2018 07:41 PM
    Part numbers D7212B, D9112B, D7212B1, D9112B1, D7212, D7412, D9112, D9124, D9412, D7212G, D7412G, D7412G, D9124G, D9412G, D7212GV2, D7412GV2, D7412GV2, D9124GV2, D9412GV2, D7212GV3, D7412GV3,D7412GV3, D9412GV3, D7212GV4, D7412GV4, D7412GV4, D9412GV4, B8512G, B9512G
    View full article
    ‎11-17-2023 10:22 PM
    Part numbers RF1000, RF3212, RF3222, RF3224
    View full article
    ‎06-29-2018 07:04 PM
    Issue What does it mean when the LED flashes on the motion (PIR)?   Solution   LED                                    Cause On                                      Unit Alarm or Stored Alarm Flashing 2                           Motion Monitor Timeout Flashing 3                           Antimask Detection Flashing 4                           PIR Self test Failure Flashing 5                           Low Input Power or Relay Failure
    View full article
    ‎06-29-2018 06:56 PM
    Issue What is the dual phone line monitor module for the D7112?   Solution   The D728 would be the dual phone line monitor module for the D7112 panel.
    View full article
    ‎06-29-2018 08:31 PM
    How to set the test report time on the 190 Test Report Timer module for the 4012/8012 panel. D4012,D8012
    View full article
    ‎06-29-2018 06:30 PM
    Part numbers D7212B, D9112B, D7212B1, D9112B1, D7212, D7412, D9112, D9124, D9412, D7212G, D7412G, D7412G, D9124G, D9412G, D7212GV2, D7412GV2, D7412GV2, D9124GV2, D9412GV2, D7212GV3, D7412GV3,D7412GV3, D9412GV3, D7212GV4, D7412GV4, D7412GV4, D9412GV4, B8512G, B9512G
    View full article
    ‎06-29-2018 06:13 PM
    Issue Trouble connecting to the D4412 with RPS / RAM IV using the DX4010i. What dip switches need to be set to make the DX4010i connect to the panel? What type of cable is needed between the DX4010i and the Laptop or PC? Solution RAMIV / RPS needs to be revision 3.6 or higher. Set the address 0 (Installer's mode) Dip Switches 6 and 8 in the off postion on the DX4010i. Use a NULL cable to connect the DX4010i to the Laptop or PC. For remote programming connection, use the RJ-16 to molex connector to the Aux / Data header. Lock the Installer or Reset Pin on the panel. In the RSP/ RAMIV Connection screen change the connection type from MODEM to ENHANCED DIRECT, then click connect. *If connected to a D4412 panel and the address is set wrong on the DX4010i then a message of "INVALID RAM PASSCODE" may be generated.
    View full article
    ‎06-29-2018 06:04 PM
    How to View the Event Log using the 540 command center with Honeywell 5800/5900 Series Panels. D540,5800B,5800B1,5900B1,5900B,5800C,5900C,5900G,5800G.
    View full article
    ‎06-29-2018 05:58 PM
    How to Activate the ALT ALARM RELAY on a D8112 Panel. When is the ALT ALARM RELAY triggered? D8112G2,D8112E1,D8112G1,D8112A
    View full article
    ‎06-29-2018 05:50 PM
      Issue Symptom The keypad displays Oct. Relay Fault. Probable Cause The octal relay module ( DS7488 ) is defective or the wiring to the module is defective. There is not a DS7488 or a DS7488 has been removed from the system. Solution Check the wiring to the module. Enter the programming mode. This will rescan the options bus and clear the problem. Part numbers DS7400X, DS7400, DS7400Xi, DS7400XIVER2, DS7400XIVER3+, DS7400XIVER4+,  DS7488
    View full article
    ‎06-29-2018 05:43 PM
    Issue Symptom Why would the keypad display Not Ready, but no zone number is displayed? Probable Cause An invisible zone is not ready. Possible Soultion Enter a valid pin number + off to display the zone number of the invisible zone that is not ready. Part numbers DS7400X, DS7400, DS7400Xi, DS7400XIVER2, DS7400XIVER3+, DS7400XIVER4+, DS7447
    View full article
    ‎06-29-2018 05:35 PM
    Part numbers DS7400X, DS7400, DS7400Xi, DS7400XIVER2, DS7400XIVER3+, DS7400XIVER4+, DS7430, DS7436, DS7432, DS7433, DS7460, DS7465, DS7460i, DS7465i
    View full article
    ‎06-29-2018 05:26 PM
    Issue How is the DS7432 eight input remote module interfaced with DS7400 series panels? Solution The DS7432 eight input remote module is interfaced with DS7400 series panels thru either the DS7430 (single mux bus) or DS7436 (dual mux bus) Multiplex Expansion Module. Connect the mux bus + terminal to the DS7432 module bus + and the respective mux bus - terminal to the DS7432 module bus - terminal. DS7432 is powered from Aux power from the DS7400(or X, Xi) panel terminals 7 (aux -) and 8 (aux +).  Connect power to DS7432 Power +, -. Part numbers DS7400X, DS7400, DS7400Xi, DS7400XIVER2, DS7400XIVER3+, DS7400XIVER4+, Ds7432, DS7430, DS7436
    View full article
    ‎06-29-2018 05:41 PM
    What programmmer was used to program the wireless transmitters point transmission interval, point #, and house code on a D7112 wireless system?
    View full article
    ‎06-29-2018 05:21 PM
    Issue Panel history shows a failure 3.   Solution   If panel is programmed to do a history dump to WDSRP but failed to communicate via the phone line that is programmed for remote callback, the panel will initiate a failure 3 trouble.   Part numbers DS7400X, DS7400, DS7400Xi, DS7400XIVER2, DS7400XIVER3+, DS7400XIVER4+,
    View full article
    ‎06-29-2018 05:18 PM
    Issue Does the panel need to see a perimeter point faulted during the exit delay when arming All On to actually fully arm the system and not just Part Arm?   Solution   When the ARMING OPTIONS prompt Enable 'All On - No Exit ' feature is set to yes , the panel must see a perimeter point faulted during the exit delay in order to fully arm . If the panel does not see that , the panel will switch to PART ON to prevent a false alarm.
    View full article
    ‎06-29-2018 04:46 PM
    Issue Multiplex troubles and loss of communication to devices.   Solution   Perform the Following Troubleshooting steps 1. Check the voltage on the Mutilplex Bus 2. If the Voltage is 12VDC 3. Check and make sure the panel is out of programmer’s mode 4. Look for duplicate addresses 5. *Disable Bus lock 6. Make sure 12VDC is not connect to the Multiplex bus If the Voltage is 0 - . 3VDC 1. Check for Shorts on the multiplex loop 2. Check for reverse polarity to devices 3. If the device require diodes make sure the cathode side is on the positive side. * To Disable Bus Lock 1. Enter in to Programmers Mode  by code + #0 2. Type in 9999 *5 Part numbers DS7400X, DS7400, DS7400Xi, DS7400XIVER2, DS7400XIVER3+, DS7400XIVER4+, DS7430, DS7436
    View full article
    ‎06-29-2018 04:18 PM
    Issue This is a report that is generated when the system is armed and Closing Ring Back is enabled but the closing report is not. The Report 0 occurs because the panel does a phone check to see if dial-tone  is detected. If dial tone is not detected at the time the panel is armed it will display a Communication Fault on the Keypad it will generate this error in the History buffer. How are Report Fail 0 messages prevented? Solution To prevent these errors from occurring perform the following steps: On the DS7400/X version 1.xx 1. Enter in program mode by entering in the program PIN + #0 2. Depress 0011 03# 3. Hold the * key for 3 seconds to exit out of Program mode  On the DS7400Xi  Version 2.xx and Ver 3+ 1. Enter in program mode by entering in the program PIN + #0 2. Press 0000 03# 3. Hold the * key for 3 seconds to exit out of Program mode On the DS7400Xi Ver 4 1. Enter in program mode by entering in the program PIN + #0 2. Press 0000 03# 3. Hold the * key for 3 seconds to exit out of Program mode Part numbers DS7400X, DS7400, DS7400Xi, DS7400XIVER2, DS7400XIVER3+, DS7400XIVER4+,
    View full article
    ‎06-29-2018 04:14 PM
    Issue Why does an invisible or silent zone activate the alarm output? Solution Probable Cause The output is programmed as "latch on alarm" (0) Possible Solution Program the output to follow zone alarms ( 6 ). Part numbers DS7400X, DS7400, DS7400Xi, DS7400XIVER2, DS7400XIVER3+, DS7400XIVER4+,
    View full article
    Top Contributors
    Icon--AD-black-48x48Icon--address-consumer-data-black-48x48Icon--appointment-black-48x48Icon--back-left-black-48x48Icon--calendar-black-48x48Icon--center-alignedIcon--Checkbox-checkIcon--clock-black-48x48Icon--close-black-48x48Icon--compare-black-48x48Icon--confirmation-black-48x48Icon--dealer-details-black-48x48Icon--delete-black-48x48Icon--delivery-black-48x48Icon--down-black-48x48Icon--download-black-48x48Ic-OverlayAlertIcon--externallink-black-48x48Icon-Filledforward-right_adjustedIcon--grid-view-black-48x48IC_gd_Check-Circle170821_Icons_Community170823_Bosch_Icons170823_Bosch_Icons170821_Icons_CommunityIC-logout170821_Icons_Community170825_Bosch_Icons170821_Icons_CommunityIC-shopping-cart2170821_Icons_CommunityIC-upIC_UserIcon--imageIcon--info-i-black-48x48Icon--left-alignedIcon--Less-minimize-black-48x48Icon-FilledIcon--List-Check-grennIcon--List-Check-blackIcon--List-Cross-blackIcon--list-view-mobile-black-48x48Icon--list-view-black-48x48Icon--More-Maximize-black-48x48Icon--my-product-black-48x48Icon--newsletter-black-48x48Icon--payment-black-48x48Icon--print-black-48x48Icon--promotion-black-48x48Icon--registration-black-48x48Icon--Reset-black-48x48Icon--right-alignedshare-circle1Icon--share-black-48x48Icon--shopping-bag-black-48x48Icon-shopping-cartIcon--start-play-black-48x48Icon--store-locator-black-48x48Ic-OverlayAlertIcon--summary-black-48x48tumblrIcon-FilledvineIc-OverlayAlertwhishlist